Ufer grounds are based on the "parallel" principle. The ft^2 area of the slab in contact with the earth basically makes many parallel grounds; as well as the "always moist" aspect of concrete. (Herbert G. Ufer created his namesake to ground ammunition bunkers in the Southwest against lightning strikes.)
POCO does the same thing. Multiground Neutral has in effect thousands of parallel grounds per mi^2 of service area. Your Ufer/rod/pipe is part of the big picture.
As for SWER, the HVDC Pacific Intertie has a large ground at each end, even though it's {?now} balanced. Good place to dump faults when required.
https://en.wikipedia.org/wiki/Pacific_DC_Intertie
The grounding system at Celilo consists of 1,067 cast iron anodes buried in a two-foot trench of petroleum coke, which behaves as an electrode, arranged in a ring of 2.02 mi (3,250.87 m) circumference at Rice Flats (near Rice, Oregon), which is 6.6 mi (10.6 km) SSE of Celilo. It is connected to the converter station by two aerial 644 mm2 ACSR (aluminum conductor, steel reinforced) conductors, which end at a "dead-end" tower situated at 45.497586°N 121.064620°W.
&
The Sylmar grounding system is a line of 24 silicon-iron alloy electrodes submerged in the Pacific Ocean at Will Rogers State Beach[4] suspended in concrete enclosures about one meter above the ocean floor. The grounding array, which is 30 mi (48 km) from the converter station and is connected by a pair of 644 mm2 ACSR conductors, which are in the sections north of Kenter Canyon Terminal Tower at 34°04′04.99″N 118°29′18.5″W installed instead of the ground conductors on the pylons. It runs from Kenter Canyon Terminal Tower, via DWP Receiving Station U (Tarzana; a former switching station), Receiving Station J (Northridge) and Receiving Station Rinaldi (also a former switching station) to Sylmar Converter Station. On the section between Receiving Stations J and Rinaldi, one of the two shielding conductors on each of two parallel-running 230 kV transmission lines is used as electrode line conductor.