So. If it serves the appliance it is still an individual circuit.
Branch Circuit, Individual. A branch circuit that supplies
only one utilization equipment.
I have a 20 amp circuit serving my inside AHU and there is a condensate pump also. Violation?
422.12 Central Heating Equipment. Central heating
equipment other than fixed electric space-heating equipment
shall be supplied by an individual branch circuit.
Exception No. 1: Auxiliary equipment, such as a pump,
valve, humidifier, or electrostatic air cleaner directly associated
with the heating equipment, shall be permitted to be
connected to the same branch circuit.
Not a vilolation if it meets conditions of the exception.