You're right.
I don't understand why you would want to stick with a rule that has been clearly shown to be violated.
Actually, I did a bit more.
The curves go to 100 seconds, and, despite what you said, they most certainly have not leveled other than just about for the 1A fuse. I'll come back to that.
For all the others, they are continuing to reduce in value and no doubt would continue to do so beyond that 100 seconds.
So I projected them to 600 seconds - it was as far as I could on the page on which I printed the curves - still a long way short of your one hour.
As far as I could tell, every one would fail your 140% test with the
possible exception of the 1A fuse. And even that is marginal. The scales are logarithmic and, when you take that into account, it's by no means certain that it would survive for an hour.