Fuse failures

Status
Not open for further replies.
T

T.M.Haja Sahib

Guest
Bes:
I want to submit that, unfortunately,you too do not seem to grasp the purpose of test-1 on a fuse.Do you?
 

iwire

Moderator
Staff member
Location
Massachusetts
Bes:
I want to submit that, unfortunately,you too do not seem to grasp the purpose of test-1 on a fuse.Do you?

And I submit that you seem to be over looking the fact that a fuse that can hold 140% of its rating for one hour is not a normal fuse. All the fuses I install would fail the test you describe below.


First test.The fuse should not blow for current up to 140% of its rated current within one hour.
 

Besoeker

Senior Member
Location
UK
The reason is the curve become almost parallel to the vertical line erected at 140% of rated current of each fuse.
Look again at the curve for the 3A fuse. At what current does it cross the 100 second line?
It's a simple question and I have posted sufficient information for you to work it out.
Can you?
And, if so, what is it?
And how does that relate to your 140%?
 

iwire

Moderator
Staff member
Location
Massachusetts
Is it a conviction or a confirmation?:D


You propose that all fuses should be tested at 140% of there rated value for 1 hour.

What I am telling you is most standard fuses in use in America would fail before that hour.

There should fail be for that hour

If they did not fail before the hour was up there is something wrong with the fuse.

Why not pick a particular fuse that you would work with, post its specifications and we can discuss it?
 
T

T.M.Haja Sahib

Guest
What I am telling you is most standard fuses in use in America would fail before that hour.

Take for example any one fuse rating you illustrated few posts back and work the time for the fuse to blow when 140% current passes through it.Say it is 20A common fuse.The 140% current is 28A.From its fuse curve,you may find time for the fuse to blow for that 28A.
 
T

T.M.Haja Sahib

Guest
explain what you think is misleading about.

Your 'demonstration' that a 3A common fuse would blow at 4.2A within one hour and so the 140% rule is false is misleading.

The test is actually carried out at about 140% of fuse rating.If the fuse curve shows it would below at 140% exactly,slightly reduce the percentage;fix it at 135%, for example, for all of the fuses in the batch under test.

Same is the case for 160% rule.
 

Besoeker

Senior Member
Location
UK
Your 'demonstration' that a 3A common fuse would blow at 4.2A within one hour and so the 140% rule is false is misleading.
The rule clearly is false for that fairly common fuse. The curve shows it would blow at 4A after 100 seconds.
I don't see anything whatsoever misleading about that. It is what it is.

So what now do you say about your comment:
Any one fuse curve negating the tests would do.
We've found one.

The test is actually carried out at about 140% of fuse rating.If the fuse curve shows it would below at 140% exactly,slightly reduce the percentage;fix it at 135%, .
I think that's called moving the goalposts.
 

Besoeker

Senior Member
Location
UK
You're right.
I don't understand why you would want to stick with a rule that has been clearly shown to be violated.
Actually, I did a bit more.
The curves go to 100 seconds, and, despite what you said, they most certainly have not leveled other than just about for the 1A fuse. I'll come back to that.
For all the others, they are continuing to reduce in value and no doubt would continue to do so beyond that 100 seconds.
So I projected them to 600 seconds - it was as far as I could on the page on which I printed the curves - still a long way short of your one hour.
As far as I could tell, every one would fail your 140% test with the possible exception of the 1A fuse. And even that is marginal. The scales are logarithmic and, when you take that into account, it's by no means certain that it would survive for an hour.
 
T

T.M.Haja Sahib

Guest
You're right.
I don't understand why you would want to stick with a rule that has been clearly shown to be violated.
Actually, I did a bit more.
The curves go to 100 seconds, and, despite what you said, they most certainly have not leveled other than just about for the 1A fuse. I'll come back to that.
For all the others, they are continuing to reduce in value and no doubt would continue to do so beyond that 100 seconds.
So I projected them to 600 seconds - it was as far as I could on the page on which I printed the curves - still a long way short of your one hour.
As far as I could tell, every one would fail your 140% test with the possible exception of the 1A fuse. And even that is marginal. The scales are logarithmic and, when you take that into account, it's by no means certain that it would survive for an hour.

The fuse curves presented so far in the thread is up to 200 seconds only.If more time period were present,you could have made better decision.For this purpose,I provide a link for your eyes only.Take a look at page 147 and offer more comments.

http://www.fmccrustel.ru/pdf/BS88/BS88.pdf
 

Besoeker

Senior Member
Location
UK
The fuse curves presented so far in the thread is up to 200* seconds only.
My comments related to the curves kindly provided by iwire and your
And your
Any one fuse curve negating the tests would do.
We may have found several from that one sheet alone that negate the tests.

*Clearly, you missed post #71.
And, just for the record, I'm well aware of BS88 fuse characteristics. I have a copy of BS7671 on my desk both here at home and in my office at work.
Being British and an electrical engineer it would shameful if I did not.
 
Status
Not open for further replies.
Top