I am told the center pole is an EGC. Anyone have a code section to cite here?
That would allow the switch not the fuse.Originally posted by peter d:
But does 250.124 (B) allow this?![]()
Edit: I don't think so because this is more than just a switch, it's an OCPD.
Did that same person ask you to verify your banking information, and promise you a share in a $44 million overseas deposit they are trying to make?Originally posted by iwire:I am told the center pole is an EGC.
Well there is no conduit coming from the source, this disconnect is fed from the rear with SE cable.Originally posted by charlie b:
I think it more likely that the center pole is the neutral, and that the conduit is serving as the EGC.
Pete that is better than I have come up with so far.Originally posted by peter d:
Is this a trick question Bob. I'm having a hard time finding a reference. So far all I can come up with is 250.4(A)(5) because this is not a "permanent, low impedance circuit."
Well, I tried some more and that's still the best I can come up with.Originally posted by iwire:
Pete that is better than I have come up with so far.
Originally posted by peter d:
Wes, I don't understand how those code sections are remotely applicable.![]()
First this section requires that, ?shall be installed in a manner that creates a permanent, low-impedance circuit .? The fuse would be anything but ?permanent.?(5) Effective Ground-Fault Current Path. Electrical equipment and wiring and other electrically conductive material likely to become energized shall be installed in a manner that creates a permanent, low-impedance circuit facilitating the operation of the overcurrent device or ground detector for high-impedance grounded systems. It shall be capable of safely carrying the maximum ground-fault current likely to be imposed on it from any point on the wiring system where a ground fault may occur to the electrical supply source.