Thats obvious- and something you must take into account when doing coordination studies.
If there is no overhead portion. An underground to overhead setup without a recloser would require auto-reclosing the cable- that is unless the cable is first in line and you have MHO impedance elements which will drive the relay to lockout should it pickup for the cable zone- at least the the first 90% of the cable anyway.
Thats true- but is such speed and accuracy really needed all the time?
Very valid- which is why you want to have single phasing protection at the MCC / 480 volt portion of the systems. How many POCOs feed large motor customers with fuse protected risers and transformers?
Substation breaker is always a breaker- but down stream there is lots of room to chose.
obvious to some
you are stating the obvious
and you will still not match a relay with a fuse
????
yes
unless you can tolerate damage
but up stream is a cb
and for large industrial users they get a util sub...w/cb
there are numerous reasons it is not done
you are asking open ended questions that need specifics to be answered
and those have been answered in dozens of texts and decades of practice
do you design T&D grids?
hi Z gnd fault
a fuse will sit there all day
a cb with ct's configured for 0 seq will trip and clear
the most common fault, as 90% of all util dist faults