Fuses vs Circuit breakers in switch gear

Status
Not open for further replies.

mivey

Senior Member
I honestly do not know :(

Though I doubt I will exceed 10,000amps.
Current limiting fuses are often used to reduce risk of transformer rupture for faults closer to the substation.

I have never used them on outdoor MV for arc flash reduction but I suppose you could if you found a benefit.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Current limiting fuses are often used to reduce risk of transformer rupture for faults closer to the substation.

I have never used them on outdoor MV for arc flash reduction but I suppose you could if you found a benefit.

Seen some POCOs add CLF on pole pigs near the sub- that would make sense.
 

mivey

Senior Member
What would you say about 25kv or maybe even 34.5kv? Also can a modified saturation curve prevent it?
I would check for favorable conditions, especially on a 34.5kV system.

Don't know about the sat curve, would have to check.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
The smaller the transformer the greater the risk but usually starting around 4kA to 6kA of fault can be a concern target.

Did not know this- much thanks. Up to 10ka I will just spec a K or T link... I never gave this much thought. :eek:

I would check for favorable conditions, especially on a 34.5kV system.

Don't know about the sat curve, would have to check.


Thanks :)
 