If you can do that, why do you say:
Are the demand readings from the customer only on an aggregate basis, not per line? If only on an aggregate basis, for an open delta, how do you use demand readings to tell the required relative size of the single phase (lighting) and 3 phase (power) pots?
Cheers, Wayne
We don’t.
The meter returns peak kW only.
From there it’s up to us to investigate if it’s single or three phase loading.
Quite honestly most of our transformers are oversized anyway.
If I run an overload report and plug in something like 90% loading, I only get about 30-40 spit out. A lot of those are transformer sizes entered wrong. We had a guy that would put a “1” in the size field if he didn’t know the true size. It won’t accept null.
All he had to do was return the sheet back to the field guy that finished the job to get the correct size.
Most are residential. But in winter time we can run them a little overloaded for a real long time. Summer, we better go look.
Nothing worse than a hot customer that doesn’t have AC because of a transformer going out.