I am not familar with the code rule that requires a 20 ampere circuit for commerical garages. Can you post the section, thanks.Originally posted by cormier_paul:
Remember this applies to residential occupancies, and that commercial garages would require 20 amp circuits.
There is another section of code you might want to consider. If the garage is detached, there are some added requirements for circuits/feeders. I believe it's section 240 of the code (I don't have the handbook in front of me). Anyway, it's the article called "outside feeders and branch circuits".Originally posted by shaun:
Does the branch circuits in the garage have to be 15a or 20a circuits. Or 14awg or 12awg? Also would it depend on whether or not the garage is being finished or unfinished?
Sounds like you're referring to 225.39 Rating of Disconnects. I don't see how this would apply to the garage feeder size. This Article is for the sizing of the required disconnecting means not the feeder.Within that article, there is a section that says if a detached building has one circuit, it must be at least 15A; if there are two circuits, the feeder must be at least 30A; in all other cases, the feeder size must be at least 60 A.
I agree with your suggestion, it is apparent that some choose to always search out the code so they can sleep at night knowing that they pulled off a job that met the code! Hurray.. for all of you who put your work in by meeting the minimum requirements, why grovel over 15a or 20a,#14 or #12,wouldn't you sleep better if you guys knew that you had exceeded the code.if your confused over 15a or 20a in a residential garage, wait till you size a service for a 27 story building with a commercial parking garage attachedOriginally posted by charlie b:
No. But it would be a good design choice. So too, in my opinion, would be to use #12 and 20 amp breakers, even if a #14/15 amp is allowed. Note, "design choice," not code requirement. The trick is to convince the owner/builder that it is a good idea, and worth the extra costs.
This is not that difficult of a task, but I must ask, who seals your designs?wait till you size a service for a 27 story building with a commercial parking garage attached
GE Finance, GE Industrial(If the owner doesn't want to pay for it, then why should you oblige them to compromise the integrity of their existing service(poor practice), Nothing is impossible to sell as long as it is justified and legal, as are all installations specified by the NEC, all I'm saying is the code is our bargaining chip, otherwise everyone could perform this vocation. Because most electrical installations are required to conform to the NEC, then it is our responsibility to the customer and to ourselves to ensure that they are getting what they paid for. If the customer paid for a compromised system, then someone isn't doing their job well enough and is lacking in their duties as a licensed professional. We need to continue to push the envelope on safety and integrity. These qualities will help separate you from the "fly by nights" and will increase your profit margin.Originally posted by roger:
Oneway, I think most people sleep well knowing they have met the code if that is all the owner wanted to pay for.
On the other hand, I know I would sleep better if the owner wanted to pay for a larger circuit and increase my profit margin. (not that there would be enough to worry about in this scenario)
This is not that difficult of a task, but I must ask, who seals your designs?wait till you size a service for a 27 story building with a commercial parking garage attached
Roger
They apply an engineering stamp to your prints?Originally posted by OneWay:
GE Finance, GE Industrial