Heres the situation.
1. Garage detached from house and feed from the panel located in the house.
2.4 conductor feeder installed. 2 ungrounded, 1 grounded, 1 equipment gound.
Is this concidered a serperate service?
Does this require a ground rod at the garage?
If there are more than 6 circuits does the panel require a main breaker?
The inspector and I disagree on all 3 areas. I feel it is not a new service, since I installed 4 conductors it does not need a ground rod and it does not require a main breaker because there is one at the house panel.
The inspector won't move and claims he is using the 2002 NEC.
1. Garage detached from house and feed from the panel located in the house.
2.4 conductor feeder installed. 2 ungrounded, 1 grounded, 1 equipment gound.
Is this concidered a serperate service?
Does this require a ground rod at the garage?
If there are more than 6 circuits does the panel require a main breaker?
The inspector and I disagree on all 3 areas. I feel it is not a new service, since I installed 4 conductors it does not need a ground rod and it does not require a main breaker because there is one at the house panel.
The inspector won't move and claims he is using the 2002 NEC.