How do you decide which pipe is going to be your 250.104(A) pipe, and which is going to be your (B) (unbonded) pipe? None of them are likely to become energized.
If it is a complete metal water piping systemgeorgestolz said:How do you decide which pipe is going to be your 250.104(A) pipe,
If it is not a complete metal water piping system.georgestolz said:and which is going to be your (B) (unbonded) pipe?
Old habits are hard to break.georgestolz said:None of them are likely to become energized.
mayjong said:In Article 90 the definition of bonded is as follows: Bonding (bonded), The permanent joining of metallic parts to form an electrically conductive path that ensures electrical continuity and the capacity to conduct safely any current likely to be imposed.
how can the "system" be bonded if it is not continuous? (as per the definition?)
mayjong said:the NEC handbook states
mayjong said:what say you?
jwelectric said:With careful reading of 250.104(A)(1) we can see that there is no requirement to bond metal water pipes. What is required is that any metal water SYSTEM to be bonded to the service grounded conductor.
Until you reach a number of posts, the forum software will not allow your post to be visible until a moderator approves it. This is the mechanism by which we enjoy a porn-free, solicitor-free, and DIY-reduced forum; so we appreciate your patience if you post close to bed-time. Stick around and you'll see your posts instantly like everyone else.mayjong said:sorry, i didn't think those posts were going through, they weren't showing up on my comp....
Natfuelbilll said:How does the NEC define SYSTEM?
jwelectric said:
Soars on Grounding published by the IAEI states that the metal gas pipes, metallic drains, metal hot water and metal cold water pipes be bonded based on Table 250.66 in addition to making the statement that the pipes be electrically continuous. Soars includes metallic air ducks, TV antenna poles and downspouts in their things to bond. They even go as far as to say on page 137 of the Eight Edition that this is a mandatory and essential requirement of the NEC.
Aren’t we glad that these other books can’t be enforced?
The only book that counts is the NEC. I have learned that when I am in doubt about a code section the ROPs is a good place to see why the Code Panel decided the way they did. The second best place to find what a consensus might be is a NEC forum such as this one.
The NEC can not regulate the plumbing codes and the code panel realizes this. The plumbing codes do not forbid the installation of non metallic pipes, fittings, devices or fixtures in a system that also has metal pipes.
The argument that the reverse could take place in a complete metal water system that is supplied by non metallic pipes, (the non metallic supply being replaced with metal pipes) is the strong arm that holds the requirement to bond based on the service in place is my understanding.
With careful reading of 250.104(A)(1) we can see that there is no requirement to bond metal water pipes. What is required is that any metal water SYSTEM to be bonded to the service grounded conductor.
mayjong said:the NEC handbook says (and this is a quote)
" all of the commentary material has been written,researched and reviewed by NFPA staff and members of the National Electric Code Commitee."
this IS an official NFPA book ( they ONLY write the NEC) if i can't use this as a reference for (and i quote) "code intent and interpretations" then why use anything?
i will agree that it seems as though the code panel ROP's and the handbook (researched,written and reviewed by NFPA and NEC Committee) contradict each other. (understatement)
i don't even disagree with your interpretation (jumper not needed)
however, until there is a clear (is any code clear?!?!? good grief!) decision,(in my mind) i will go with the most restrictive of the two
The commentary and supplementary materials in this handbook are not a part of the Code and do not constitute Formal Interpretations of the NFPA (which can be obtained only through requests processed by the responsible technical committees in accordance with the published procedures of the NFPA). The commentary and supplementary materials, therefore, solely reflect the personal opinions of the editor or other contributors and do not necessarily represent the official position of the NFPA or its technical committees. ?Registered Trademark National Fire Protection Association, Inc.
Mike, that would be an argument to not bother bonding anything at all.jwelectric said:If you answer yes please take a moment and explain how the hot water pipes in each unit can be energized.
True words of wisdom my friend.georgestolz said:It makes more sense to bond everything or nothing as opposed to an undefined piece of something.