georgestolz said:No, it's outlined in 250.53(D)(1), just as the heading of the picture (and the text of the section) states.
georgestolz said:
If you can't see this, I can't think of another way to express it, so I guess the discussion would be over, in that case.
Edit: I think I might draw up a few scenarios, to vote on, and to make our different interpretations more plain for discussion.
Yes George the title of the slide is 250.53 and I also understand that this bonding jumper would have to land as outlined in 250.104(A)(1) if there was no metal water pipe in contact with earth.
I understand that 250.53(D)(1) is saying that when I am bonding the water pipe to the electrode I can have nothing that breaks the continuity of the path from the point I bond to the pipe and the point I connect to the electrode such as meters, filters, pressure limiting devices or things such as these.
If you would be so kind and being you have nothing to do please answer these questions for me.
Using Mike?s slide; could I remove the jumper that is across the Removable Device and replace it with one that runs all the way back to the panel?
Could I remove the jumper that is across the Removable Device and run a jumper from the panel to any accessible point on the water system?
Just what is being bonded together with the jumper that is across the Removable Device?