Sorry guys, my set of ROPs and ROCs starts with the 84 code.
Don
Don
I think JT's older collection of ROPs and ROCs might be on papyrus scrolls.don_resqcapt19 said:Sorry guys, my set of ROPs and ROCs starts with the 84 code.
Don
jwelectric said:(1) Continuity. Continuity Of The Grounding Path or the bonding connection to interior piping shall not rely on water meters or filtering devices and similar equipment.
I can clearly see that it is the path that is requiring continuity.
Both paths require continuity. Where does each end?(1) Continuity. Continuity of <----The subject
(1.) the grounding path |
or
(2.) the bonding connection to interior piping |
shall not rely on water meters or filtering devices and similar equipment.
That could very well be.I believe that the fact that they can not control the plumbing codes they gave up on the requirement for the pipes be electrically continuous.
That would be a call on the AHJ's part. Based on the information given (no rough lengths of each component) I wouldn't even venture an opinion yet.Should these metal water pipes have been bonded back to the service with a 1/0 copper bonding jumper?
georgestolz said:That would be a call on the AHJ's part. Based on the information given (no rough lengths of each component) I wouldn't even venture an opinion yet.jwelectric said:Should these metal water pipes have been bonded back to the service with a 1/0 copper bonding jumper?
(1) Continuity. Continuity of the grounding path or the bonding connection to interior piping shall not rely on water meters or filtering devices and similar equipment.
georgestolz said:This section also deals with the bonding connection to interior piping, plain and simple. It shouldn't, but it does. Agree or disagree?
Hey George this is just what I have been saying about a metal water pipe being electrically continuous. If they want the metal water pipe to be electrically continuous they would say so just as they did in past code cycles.georgestolz said:Mike, if they wanted to say "bonding jumper" they would have.
It would be my guess that they say bonding connection because the bonding jumpers get ?connected? to the metal water pipe via a clamp.georgestolz said:Why would they say "bonding connection" and introduce confusion?
jwelectric said:Hey George this is just what I have been saying about a metal water pipe being electrically continuous. If they want the metal water pipe to be electrically continuous they would say so just as they did in past code cycles.
Are you serious? Devil's Advocacy aside, are you being honest when you say that when they refer to the "bonding connection to interior piping" they are intending to say "bonding connection to the portion of the grounding electrode suitable for interconnecting electrodes"?It would be my guess that they say bonding connection because the bonding jumpers get ?connected? to the metal water pipe via a clamp.
Maybe because a jumper is not the only method?georgestolz said:Mike, if they wanted to say "bonding jumper" they would have. Why would they say "bonding connection" and introduce confusion?
This is just what the code says in itself. It is right here;georgestolz said:Are you serious? Devil's Advocacy aside, are you being honest when you say that when they refer to the "bonding connection to interior piping" they are intending to say "bonding connection to the portion of the grounding electrode suitable for interconnecting electrodes"?
The whole of 250.53 is addressing the Grounding Electrode. (D) is addressing a metal water pipe that is being used as the electrode. (1) is addressing the point of attachment (connection) of the grounding electrode jumpers and the part of the water pipe that is the electrode itself.250.53 Grounding Electrode System Installation. (D) Metal Underground Water Pipe. Where used as a grounding electrode, metal underground water pipe shall meet the requirements of 250.53(D)(1) and (D)(2).
(1) Continuity. Continuity of the grounding path or the bonding connection to interior piping shall not rely on water meters or filtering devices and similar equipment.
Do you think that they have goofed for three straight code cycles? In the 1999 cycle 250 was completely redone.georgestolz said:That's way out in left field, IMO. It seems pretty clear to me they goofed and stuck a bonding requirement for the interior piping in the GEC area of the codebook. I mean, honestly, Mike...
Thanks Larry, I hadn?t though of that.LarryFine said:Maybe because a jumper is not the only method?
Instead of this short jumper I could have ran a bonding jumper to anywhere that is accessible on the metal water pipe back to the panel.250.104(A)(1) General. Metal water piping system(s)?.. shall be bonded?.. to the one or more grounding electrodes used.
No, it's outlined in 250.53(D)(1), just as the heading of the picture (and the text of the section) states.jwelectric said:The other part of this picture I see a bonding jumper (across the removable device) that is ran from the interior metal water pipe as outlined in 250.104.
It's a good way to kill a Monday, though, isn't it?Pierre C Belarge said:I realize with 20 different minds, sometimes there will be 20 different ideas. I think way too much "thinking" is going on in this thread...