The area where the wiring currently ends will become parking and/or sidewalk, adjacent to the new building.
Article 514 states that any underground wiring passing under or through the Class I, Div 1 or 2 areas is to be considered in a Class I Div 1 area at least until it emerges above grade, where it must be sealed.
BTW, significant spillage during vehicle fueling is common, even with the newest dispensers. Some are much worse than others. All of the spillage does not evaporate, as concrete is fairly porous. Although an epoxy sealant would probably help, it could create static electricity issues, not good when fueling with gasoline.
Article 514 states that any underground wiring passing under or through the Class I, Div 1 or 2 areas is to be considered in a Class I Div 1 area at least until it emerges above grade, where it must be sealed.
BTW, significant spillage during vehicle fueling is common, even with the newest dispensers. Some are much worse than others. All of the spillage does not evaporate, as concrete is fairly porous. Although an epoxy sealant would probably help, it could create static electricity issues, not good when fueling with gasoline.