Utilities often run wye-wye transformers, which do not have the same problem.Why is it okay for the utility?
And when they use wye-delta they are in a position to measure, analyze and most importantly do something about voltage imbalance in the wye.
POCOs also have more pressing reasons to use wye primaries since, I am told, it reduces the likelihood of ferroresonance problems at high voltages.