Did you read the notes
Notes to 250.66Now I am confused, why would you double it? I thought you were agreeing that you size it based on one set?
Notes:
1. If multiple sets of service-entrance conductors connect directly to a
service drop, set of overhead service conductors, set of underground
service conductors, or service lateral, the equivalent size of the largest
service-entrance conductor shall be determined by the largest sum of
the areas of the corresponding conductors of each set.
2. Where there are no service-entrance conductors, the grounding
electrode conductor size shall be determined by the equivalent size of
the largest service-entrance conductor required for the load to be
served.