GEC size may vary?
Just want to check my thinking here. Depending on how a service is configured, the same size service may have a different size gec per 250.66.
Example: 400 amp service, one service disconnect, 500kcmil, = 1/0cu gec per 250.66.
(2)200 amp disconnects, 3/0 - 167800kcmil x 2 = 335600. 350kcmil = #2cu gec per 250.66
Thanks, Buck
[ May 18, 2005, 02:41 PM: Message edited by: buck33k ]
Re: GEC size may vary?
Originally posted by dillon3c:
Buck you thinking,math, method and sizing are correct.Useing table 8 & 250.66
Can you please translate Yoda to English?
Larry,
I see you pasted quote..Is there something explained,between the two of these postings that you didn't understand sir? :confused: ?
--->dillon3c
Dillon3c tends to write in incomplete sentences, lending to a "Yoda" like post. :D
Wise is he, and friendly too, no offense intended to him I am sure. :D
Larry, certainly you knew what Dillon was saying, I mean after all those years with Moe, Shimp, and Curly, anyone else could be understood. :D
Roger