GEC size may vary?

Status
Not open for further replies.
Just want to check my thinking here. Depending on how a service is configured, the same size service may have a different size gec per 250.66.

Example: 400 amp service, one service disconnect, 500kcmil, = 1/0cu gec per 250.66.

(2)200 amp disconnects, 3/0 - 167800kcmil x 2 = 335600. 350kcmil = #2cu gec per 250.66

Thanks, Buck

[ May 18, 2005, 02:41 PM: Message edited by: buck33k ]
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Re: GEC size may vary?

Originally posted by dillon3c:
Buck you thinking,math, method and sizing are correct.Useing table 8 & 250.66
Can you please translate Yoda to English?
 

dillon3c

Senior Member
Re: GEC size may vary?

Larry,
I see you pasted quote..Is there something explained,between the two of these postings that you didn't understand sir? :confused: ?


--->dillon3c
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Re: GEC size may vary?

Dillon3c tends to write in incomplete sentences, lending to a "Yoda" like post. :D

Wise is he, and friendly too, no offense intended to him I am sure. :D
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: GEC size may vary?

Larry, certainly you knew what Dillon was saying, I mean after all those years with Moe, Shimp, and Curly, anyone else could be understood. :D

Roger
 