GEC tap bonding
This is true. I dont know if its the same for every ec here but grounding is basically pick 2 out of 3 cw bldg steel and ground rod. You choose.
That is ridiculous, NEC states what qualifies for a grounding elecrode and tells you if it is present you must use it. If no naturally existing electrodes are present then it tells you you need to install at least one made electrode. Only naturally existing electrode that needs supplementing is the water pipe electrode, otherwise I have done many new buildings that have just a CEE and no other electrodes.
NEC says you could run a separate GEC to each service disconnect, a common GEC with taps to each service disconnect, you could also run a single GEC to the CT cabinet, the place where service drop attaches to the service conductors, or any other common point between. Local rules could be different, but that is your main choices in NEC.
Yep ive read that article. But you know ahj
My guess is he is talking about multiple service disconnecting means and a tap from each to a common GEC.
I think he can splice these on a bus bar, but other splicing methods would need to be irreversible methods, so the split bolts may not be compliant.
hey kwired. I believe we already discussed this and a "loop" or "daisy chain" GEC is not allowed in a multiple service disconnect setup. The way I beat the split bolt issue was that I ran the GEC unspliced and just sliced the insulation of the conductor. I then ran a jumper from grounded busbar at each panel and attached to GEC via split bolts. No splicing of GEC:D.
Um....not all AHJ's are close minded so let's not loop them all in the "BUNCH":angel:
I never knock inspectors or other electricians. As ive said before the 2 worst inspectors I have had to deal with both went crazy on me yelling codes i dont wanna know. My reply was is and will always be the same, yes sir Ill take care of it right now. Both after writing my red tag went over it and how I could do it and pass. .
True story. Im waiting on an inspector for lighting upgrade we did I see the plug by the panel is broken. I figure hell ill replace it. I look over my shoulder and the inspector starts going off about why im still working if its supposed to be ready . ( my buddy the ac guy is there laughing) so I say because some jacka $$ ac guy broke it and that I felt obligated to fix it.. no problems from then on
I don't know where you get this loop or daisy chain out of my previous comments. I was talking about what is permitted in 250.64(D)(1), where you can have a common grounding electrode conductor and taps to each service disconnecting means. That is same thing you were describing. The tap connections must be made via exothermic welding, connectors listed as grounding and bonding equipment (check your split bolts for this listing before you use them), or a busbar - with further details for minimum size of the bar.
Mr. Kwired to u and the many others here who take the time to point guys like me in the right direction. Thanx and as I really think through yalls comments on ratings , ul listings , and applied usage of materials, im seeing a whole new perspective on getting quality quantity and satisfaction with out working myself to death