The breaker has to allow the motor to start. That is the only requirement. People are questioning the 150A breaker because that breaker feels like it would be too small to allow a 100hp motor to start, but you wouldn't know for sure without comparing the motor start curve to the breaker trip curve.
Unasked in this discussion so far is if the generator itself can start the 100hp motor.
Where is this requirement in NEC 2017? “The breaker has to allow the motor to start”