Service splits at meter into 2/200 amp panels - comes out of a wiretex meter base that has a fifth aux contact/lug - right next to the meter base customer set a 24kw generac generator -
2 / 200 amp ATS or 1 / 400 amp ATS size needed on the ATS switch - customer wants whole house backed up - assuming I come straight out of auxiliary contact with 600 kcmil into ATS along with control wires from generator - generator has a 100 amp disconnect inside generator unit do I need to upsize that or is that sufficient to handle the whole load?
2 / 200 amp ATS or 1 / 400 amp ATS size needed on the ATS switch - customer wants whole house backed up - assuming I come straight out of auxiliary contact with 600 kcmil into ATS along with control wires from generator - generator has a 100 amp disconnect inside generator unit do I need to upsize that or is that sufficient to handle the whole load?