generator, 480 v, 200 amp

shalomfred

Member
Location
Dillon Montana
Occupation
electrician
I was asked to hard wire a three-phase generator for a city septic system. It is currently hooked up with a so cord. The generator has three phase wires with a chassis ground, in the service the ground is connected ground with a neutral being derived there. Do, I need to try and pull a neutral from the generator? Am I calculating the wire size correct at 250kcmils.

you all are great helping with our issues, thank you
 

shalomfred

Member
Location
Dillon Montana
Occupation
electrician
transfer switch is 3 poll, the motors (pumps) are 277v, I do not know about the generator neutral, there was generator person there calibrating the generator I could not get in there
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Then the generator would be wired as a SDS, with bonding and grounding at the building service. The neutral is only bonded are the service. There is a requirement in Art 702 for signage.
How big are the pumps? 277 is a uncommon pump / motor voltage. You asked about pulling a neutral..,it’s needed for your pumps and a a ground fault return to the generator windings
 

shalomfred

Member
Location
Dillon Montana
Occupation
electrician
will ask about the pump voltage, I will ask the generator company about the generator how it is wired, the reason I am asking these people is because this town is an hour away, I will go out if I need to, let me know other things I need to find out
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Find out size (amps) of generator circuit breaker
Does the generator have a heater and battery charger (probably) if so you will need to provide a circuit, get amps and voltage of those.
Will the owner want remote alarms and monitoring?
Get a picture of generator nameplate
If there is a control panel, get s as wiring diagram
Others will comment.,,
 

OldBroadcastTech

Senior Member
Location
Western IL
Occupation
Retired Broadcast Technician
If it is LP fired, make sure there are provisions for keeping the regulator warm (wrap in heat tape then duct tape) and be sure the heat tape is fed from the correct source ( if there is also utility power).
 