Have an existing situation with a generator in a hospital. I'm looking for a location for a new equipment ATS, can I put it in the same room as the generator.

Critical and Life Safety I realize must be isolated.

Mike
 
Mike, for a hospital there are 3 branches that need to be 2 hour fire segregated. Critical medical, life safety and essential equipment.

You can put an ATS in the same room as an eng gen however the only one you can really have in there is optional standby.
 
Military standard perhaps

Military standard perhaps

This is not my understanding. Equipment branch per 517 does not require 2 hour rating. In fact, I believe it can be run with normal circuits.

that leaves Life Safety and Critical branch which do need to be isolated and rated. Where in 517 does it state what you are asserting?

Thanks,

Mike
 
Mass Code

Mass Code

that's true but they do speak about isolation of circuits in the NEC.

I'll check my MEC. Thanks for the input.