Is it acceptable per NEC or UL to use welding cable for connection of a generator (mobile or portable) to premise wiring? Welding cable appears to be what is typically used.
Where do you find this higher rating? How does that rating work with the NEC rules?The reason welding type cable is used is because it has a higher ampere rating (allowing smaller cable to be used) ...
I don't know if I would say that most welding cable has this type of listing. I know that some does, but I have never actually seen any of it.Most welding cable that is used has some other type of listing on the insulation that is typically acceptable, such as RHH or RHW.
My point is that Type "W" cable is not "welding cable". Type "W" cable is a listed "Portable Power Cable". That is not the same item as welding cable. This is a very common misconception. The code has no ampacity table that can be used for welding cable.Table 400-5(B) clearly lists "W".
It is not all dual listed so you have to be sure you get the dual listed type if you want to avoid a red tag.We use a lot of DLO cable which I believe is also listed as RHW-2. Extra flexible and carries a higher amp rating.
Means the insulation meets specs for more than one type, as THHN or THWN or RHW or USE.Originally posted by natfuelbill:
Thank you all for your comments on this subject.
What is are you referring to with the "dual listed" phrase?
The cables that are only listed as DLO or welding cable cannot be used in NEC applications. Some of these cables are listed as DLO and RHW or welding cable and RHW. These "dual listed" cables can be used for NEC applications.What is are you referring to with the "dual listed" phrase?
Right on both counts. I just assumedOriginally posted by don_resqcapt19:
Brad,
It is not all dual listed so you have to be sure you get the dual listed type if you want to avoid a red tag.We use a lot of DLO cable which I believe is also listed as RHW-2. Extra flexible and carries a higher amp rating.
Again with the ampacity, it is not really higher as the published ampacities are based on free air and 90?C.
What the heck do you do?Master Electrician
IN-NJ-WI-CT-LA-OH-KY-TX
"Have Kleins, will travel"Originally posted by iwire:
Brad I have to ask, curiosity is getting the best of me.
What the heck do you do?Master Electrician
IN-NJ-WI-CT-LA-OH-KY-TX