steelersman
Senior Member
- Location
- Lake Ridge, VA
remember that in the OP's post that it's a 7KW generator and so is most likely not supplying the whole house just the selected circuits to be covered in power outage. These generators come with the transfer switch and panel.jwelectric said:There is no yes or no question without more information about the generator being installed.
The conductors from the generator to the building are not service conductors so they must comply with the Article covering feeders and branch circuits or Article 225.
These feeders from the generator are supplying something and this something is a structure or building.
Section .31 of Article 225 requires that a disconnect be installed for these feeders when they enter this building or structure.
For an optional standby system Section .11 of Article 702 states that a separate disconnect will not be required if the disconnect required by Section .18 of Article 445 is within sight of the building or structure.
This relief of the disconnect required by 445.18 mentioned in 702.11 must also meet all the criteria of Article 225 which would include 225.36.
Most of the optional generators being installed does not have a window that allows the disconnect required by 445.18 to be visible therefore negating the allowance found in 702.11.
Here we must understand that the words in 702.11 require that the disconnect be within sight of and not that the generator be within sight of;
702.11 Outdoor Generator Sets.
Where an outdoor housed generator set is equipped with a readily accessible disconnecting means located within sight of the building or structure supplied, an additional disconnecting means shall not be required where ungrounded conductors serve or pass through the building or structure. The disconnecting means shall meet the requirements of 225.36. (2008 code)
There has been much confusion about this disconnect for a long time as can be seen from the proposal submitted
13-181 Log #1285 NEC-P13 Final Action: Reject
(702.11, FPN (New) )
____________________________________________________________
Submitter: Mark R. Hilbert, State of New Hampshire
Recommendation: Revise text to read:
702.11 Outdoor Generator Sets. Where an outdoor housed generator set is equipped with a readily accessible disconnecting means located within sight of the building or structure supplied, an additional disconnecting means shall not be required where ungrounded conductors serve or pass through the building or structure.
Add a new fine print note to read as follows:
FPN: Section 225.36 provides additional requirements for the suitability of the disconnecting means.
Substantiation: The recommendation for this fine print note is an attempt to identify the requirements of 225.36 for the building disconnecting means, which in this case will be located at the generator, to be ?suitable for use as service equipment.? Additionally, this FPN will help identify an often overlooked requirement, clarify that even though it is remote to the building, the disconnecting means must be suitable for use as service equipment and that the requirement in 225.36 is not amended by 702.11.
Panel Meeting Action: Reject
Panel Statement: See the panel action statement on Proposal 13-131.
Number Eligible to Vote: 14
Ballot Results: Affirmative: 13
Ballot Not Returned: 1 Gustafson, R.
From Proposal 13-131
Panel Statement: The disconnect required in 700.12(B)(6) is not intended to be a service disconnect.
The code panel in their statement says that the disconnect required by 445.18 is not required to be rated as service equipment but 225.36 which governs the requirement for the feeders does.
This makes the installation of a service rated disconnect required by the rules governing the feeders that leave the generator and enter the building.
In this picture the generator disconnect that is required by 445.18 is neither in sight of nor service rated.
Therefore this installation is noncode compliant.
In order to make this installation become code compliant the rules found in Article 225 must be met. 225.31 there must be a disconnect at the building and 225.36 this disconnect must be rated as service equipment.
After a little work and the spending of more money the installation was made code compliant.