Again, my point is that power IS going to the generator.
Mark
Mark
right...my question is whether it required two ground rods....like you would usually do for a service
Again, my point is that power IS going to the generator.
Mark
250.56 requires 2 ground rods as part of the grounding electrode system. Do i need to drive 2 rods for a generator or will 1 be ok?
The lug is on the frame so as far as i can tell it's only an equipment ground for the generator frame.
......110.3(B) of the NEC, is not limited to markings on the
product, separately provided installation instructions or
information on equipment packaging. For UL certified
products, compliance also requires following the UL Guide
Information......
I do drive a rod for units with such a lug. I mention it to the customer, charge for doing it, and it's perceived as part of a well-done installation.
It certainly doesn't hurt if the genny is hit by lightning. I wouldn't want to have to defend not having driven one if such a freak accident happened.
Interestingly enough, the same thing happened to me in regard to distance between the house and the genny. The customer wanted it close for appearance sake, and the unit had no rear louvers, so the gas piping made it about 5" away.We installed a Generac earlier this year and the instructions called for a ground rod if required by local codes.
One rod, as close as possible to the pad, using maybe 1' of #6 solid.right, i was always planning on driving a ground rod i was just wondering if i needed to drive two. what do you usually do?
right, i was always planning on driving a ground rod i was just wondering if i needed to drive two. what do you usually do?