I was following the topic where an inspector required Service disconnect for generator where the conductors from generator entered a house.
http://forums.mikeholt.com/showthread.php?t=152425&highlight=briggs
If I put the ATS by the meter I would need to run the conductors from the generator around the house, couldn't enter them inside the house. As someone mentioned in the previous topic, the breaker inside generator is not rated as service disconnect. For me to put the ATS by the meter/200A service disconnect, I would need another service disconnect for the generator conductors at the generator?
"702.12 Outdoor Generator Sets. Where an outdoor housed
generator set is equipped with a readily accessible disconnecting
means located within sight of the building or structure
supplied,............
If the generator you're using has a readily accessible disconnect (that means not inside a lockable cover) (i.e Generac's is inside the gray panel on the right side of the unit. If you lock that gray cover then it's not readily accessible. BTW, it comes with a slide-in decvice that gives you the means to lock it. IMHO, just throw that away and don't tell your customer about it.) then
.......an additional disconnecting means shall not be required
where ungrounded conductors serve or pass through
the building or structure. The disconnecting means shall meet
the requirements of 225.36."
702.12 does not require me to have an OCPD in the ATS by the generator, you are correct on this, so I would only need ATS without OCPD at the generator location. But if I was to put the ATS by the meter and service disconnect, I would need another OCPD (rated as service disconnect) by the generator from what I've read in other topic.