Re: Generator Neutrals
ddderek You might have been shown diagrams that might show parallel paths on grounding system's when the system voltage is above 600 volts. MGN are multi grounded to Earth also. But it is the reason behind "why" that you must need to know. It as simple as ohms law. Take a made grounding electrode which just meets the required 25 ohm's if you take a hot conductor (120v to earth) by it self and connect it to this electrode how much current do you think will flow? only 4.8 amps. Now do this with a hot conductor that is 1kv to earth and now you have 40 amps flowing. This is the problem when mixing HV systems and low voltage systems. many of the diagrams will show extra grounding paths that are in parallel with the system neutral but some of these paths are acutely Earth which can not be used on a system that has 120 volts to earth. Now do you think this might be what you saw in those classes? as I cannot believe a electrical class would teach it's students something that not only is a direct violation of the NEC but has the potential to cause injury and or death if someone were to touch a conduit that has current running through it if the path through it was disrupted?
If you have the name of the book that we can get to confirm what you say. It would let us all learn. Or let us know that there is still some miss-informed book writers out there that maybe needs to be corrected. Before someone get's hurt by this bad information. I'm not saying your are wrong just miss-informed.
[ February 14, 2005, 07:27 PM: Message edited by: hurk27 ]
ddderek You might have been shown diagrams that might show parallel paths on grounding system's when the system voltage is above 600 volts. MGN are multi grounded to Earth also. But it is the reason behind "why" that you must need to know. It as simple as ohms law. Take a made grounding electrode which just meets the required 25 ohm's if you take a hot conductor (120v to earth) by it self and connect it to this electrode how much current do you think will flow? only 4.8 amps. Now do this with a hot conductor that is 1kv to earth and now you have 40 amps flowing. This is the problem when mixing HV systems and low voltage systems. many of the diagrams will show extra grounding paths that are in parallel with the system neutral but some of these paths are acutely Earth which can not be used on a system that has 120 volts to earth. Now do you think this might be what you saw in those classes? as I cannot believe a electrical class would teach it's students something that not only is a direct violation of the NEC but has the potential to cause injury and or death if someone were to touch a conduit that has current running through it if the path through it was disrupted?
If you have the name of the book that we can get to confirm what you say. It would let us all learn. Or let us know that there is still some miss-informed book writers out there that maybe needs to be corrected. Before someone get's hurt by this bad information. I'm not saying your are wrong just miss-informed.
[ February 14, 2005, 07:27 PM: Message edited by: hurk27 ]