mdshunk
Senior Member
- Location
- Right here.
Took some pics of a brand new generator panel install in the basement of a dwelling. The panel on the far left is the generator panel. It is fed though the "normal" breaker with the SER cable on the right protected at 100 amps. The EMT coming out the bottom goes to the generator. It has the proper hold down/interlock kit from Square D holding down the top right two breakers. The EMT ell into the side contains the circuits they transferred over from the service panel. The SER leaving out the left (origination from the main lugs of the generator panel) just goes to an outbuilding. They're using the main lugs like feed through lugs, which is fine in this case, since the panel is protected at 100 amp, and it's 100 amp SER. The next pic is the problem. The "generator inlet" is a rubber cord hanging on a hose holder, ready to put out the window and plug into a portable generator when the need arises. This is a very common installation method in my area, but I don't believe it totally squares with the NEC.