Is it permissible to run #2 AL 4 conductor for a 24 KW generator with a 100 amp breaker in generator? Can the 83 percent rule be used if the generator is supplying power to the entire house? Or would it need to be upgraded to #1 AL. 4 conductor for the full 100 amps the breaker is supplying?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Is it permissible to run #2 AL 4 conductor for a 24 KW generator with a 100 amp breaker in generator? Can the 83 percent rule be used if the generator is supplying power to the entire house? Or would it need to be upgraded to #1 AL. 4 conductor for the full 100 amps the breaker is supplying?
It's a feeder, so it's okay to use the #2al on 100a genny breakers.
 

frofro19

Senior Member
Location
VA.
Occupation
Master Electrician
It's a feeder, so it's okay to use the #2al on 100a genny breakers.
Ok, just to be clear the house service is a 200 amps with a 200 amp service rated ATS and will be going from the ATS with a #2AL to the generator.
 