tango2echo
Member
I came across a house in the field this week that had a full-load generator. The service was 200 amps. On the side of the house they had the meterbase, then the transfer switch, then a 200 amp MLO panel. The transfer switch enclosure had an interlocked main breaker and load side breaker, which supplied the lugs in the MLO panel. My question is this: You cannot manually throw the breakers in the generator transfer panel when this panel is NOT energized. Therefore, there is no main breaker on the house. Is this legal? Is my logic on this correct? Shouldn't there be a main breaker panel downstream of the transfer switch?