bbaumer said:You wire them A-light-Ground, B-light-Ground, and C-light-Ground
As explained in the corner grounded delta thread you have no reference to ground so your phase to ground reading will be unpredictable under normal conditions but likely lower than 480V. You are "capacitively coupled" to the earth only. You could read anywhere from probably less than 100V to close to 480V or maybe even higher.
Not capacitively coupled; there is a resistive path from "ground" through the lamps, so unless you have a fault then a phase to ground voltage will be the same for each phase, assuming you have equal wattage lamps.