One way to look at that is look at the trip time, and amperage it takes to trigger the trip time;From what I have heard, the ground fault protection in the charge controller is equipment level, not personnel level. Probably why they have a lot of nuisance tripping.
for a standard 2 pole residential breaker to trip in 2 seconds it takes about 3 times the handle rating.
Say an appliance develops say a 2.6k ohm resistance fault to equipment ground, and say we don't want that lasting more than 2 seconds.
That fault would need to melt down to about 1.6 ohms to pull 3 X 50A or 150 Amps so you can trip a 2 pole 50A breaker in 2 seconds.
A standard off the shelf 30mA GFPE breaker must trip in 2 seconds at 150% of 30 miliamps (mA) or 45mA (0.045 Amps)
A GFCI breaker will trip 313ms with the same ground fault.
I can see the concern over regular breakers, with all the electronics in everything, but the difference between the GFCI and the GFPE breaker only 1.6 seconds and about 40ma of exposure during that time.
That means alot if your in a pool or lake but not much for 240V equipment.