First off, I am a construction manager, not an engineer. Been doing this for 30 years, so more versed on electrical than most CM's.
Had an inspection on a project in Royal Oak, MI for a dialysis clinic. The inspector is requiring a 5 mA protection for all GFCI breakers due to a 65 kAIC rating. They are saying this cannot be done inside the panel (breakers) and suggested installing GFCI receptacles. Understand that I can install a GFCI receptacle at first device location on circuit. Eaton did perform a power study for faults.
Looking for clarification on:
1. Is this a code requirement?
2. Explain why a GFCI breaker is not sufficient.
3. Was the electrical engineer at fault for specifying GFCI breakers?