What are these used for?
RC
RC
What are these used for?
RC
What are these used for?
RC
...... I believe in 2008 the zGFCI cannot be under the tub
You never heard of a zgfci. :grin: I should have stated the art for othersThat would be a new one on me!
680.71 Protection.
Hydromassage bathtubs and their associated electrical components shall be on an individual branch circuit(s) and protected by a readily accessible ground-fault circuit interrupter. All 125-volt, single-phase receptacles not exceeding 30 amperes and located within 1.83 m (6 ft) measured horizontally of the inside walls of a hydromassage tub shall be protected by a ground-fault circuit interrupter.
You never heard of a zgfci. :grin: I should have stated the art for others
Accessible, Readily (Readily Accessible). Capable of being reached quickly for operation, renewal, or inspections without requiring those to whom ready access is requisite to climb over or remove obstacles or to resort to portable ladders, and so forth.
Some of those tub surrounds are not very easily removed, esp. by homeowners. With the definition of readily accessible I would say that under the tub is not readily accessible.
I avoid it also with a dead front GFCI on the wall near the tub. But if the tub has any surround at all I don't see how you can say it would readily accessible under the tub. The definition says you cannot remove obstacles to get to the device to be readily accessible. How do you argue that? I just don't see it as complying.
Yes it is my opinion but it appears the wording is there to support that but as everything in the NEC one could interpret things very differently.....
....In either case I think a GFCI under the tub is a bad install.
Not being disrespective here, Dennis, but that is only your opinion.
17-164 Log #2343 NEC-P17
Final Action: Accept in Principle
(680.71)
____________________________________________________________
Submitter:
Andre R. Cartal, Princeton Borough Building Dept.
Recommendation:
Add new text:
A GFCI receptacle shall not be located in the tub motor space or cavity.
Substantiation:
The installation of a GFCI type receptacle in the tub motor
space is not apparent to the average homeowner as evidenced by the many
complaints received in our office. Even if the tub occupant is aware of the
location of the receptacle, it does not seem appropriate to expect a person to
exit the tub and remove the side of the tub or the access panel to reset the
receptacle.
Panel Meeting Action: Accept in Principle
Panel Statement:
See panel action on Proposal 17-165.
Number Eligible to Vote: 11
Ballot Results:
Affirmative: 11
____________________________________________________________
Final Action: Reject
(680.71)
________________________________________________________
Submitter:
Frederic P. Hartwell, Hartwell Electrical Services, Inc.
Comment on Proposal No:
17-165
Recommendation:
1. Revise the first sentence as follows:
Hydromassage bathtubs and their associated electrical components shall bemm (1 ft) of a service access opening.
on a dedicated circuit and protected by a ground-fault circuit-interrupter.
2. Add the following sentence to 680.73 at the end:
Where the hydromassage bathtub is cord- and plug-connected, the receptacle
shall be installed so that its face is within direct view and not more than 300
Substantiation:
The proposed requirement for “readily accessible” is
excessive, since this device will not need to be reached in an emergency. On
the other hand we routinely see devices so well concealed that two flashlights
and a mirror are needed to find them, and a contortionist is required to
disconnect the tub. This language refers to a receptacle and not a GFCI device
because the issue is the disconnect ability regardless of the type of device.
Many tubs are protected by a GFCI circuit breaker, for example.
Panel Meeting Action: Reject
Panel Statement:
With regard to the first item, GFCIs are required to be tested
on a monthly basis and therefore must be accessible to be tested.
With regard to the second item, the recommendation is not specific as to
whether the outlet is located internal or external to the access compartment.
Number Eligible to Vote: 11
Ballot Results:
Affirmative: 10
Ballot Not Returned: 1 Gill, C.
In my opinion Dennis' opinion is the opinion of the CMP. :grin:
From the ROP
Now the ROC
I think it is clear the CMP does not want the GFCI under the tub.
[/left]
So how are you going to properly disconnect the tub 'in an emergency'?
I have no idea what you're asking about or how it fits into this discussion.![]()
Think of it as a feed-through GFCI receptacle without the slots.What are these used for?
Are the bodies of those items required to be readily accessible, or merely their exposed front parts?By your definition then, breakers in a panel are a Code violation because you must remove the panel cover, and possibly a deadfront, to access them. As well as devices in a box, as you would need to remove the cover plate.
..........Are the bodies of those items required to be readily accessible, or merely their exposed front parts?