nietzj
- St. Paul, Minnesota
- Electrician
422.5 (A) tells me I need to provide GFCI protection for certain appliances which are listed 1-7. I thought by hard wiring the appliance I wouldn't need to worry about any receptacle requirements of 210.52 (B) This is not a dwelling. Of the equipment listed in 422.5 (A) the closest item listed is # 7 dishwasher which does require GFCI class (A) protection of the branch circuit. (I'm connecting a 3 phase 20 amp oven which also has gas and water connections so it's similar to a dishwasher.) Since the code does not list my oven as needing GFCI protection can the AHJ simply say it's similar enough so yes you need GFCI? The bigger issue is if I install a GFCI Class (A) breaker it's designed to trip at 4-6ma. This appliance has more like 45-ma so it instantly trips the breaker so it will not work. Seems like a guy could argue he's following the code and the AHJ can say I consider this as a dishwasher.... is there an answer?