Hello, wondering if you guys can lead me to the correct direction. I'm working on a project that has a 3000 amp 120/208 volt 3 phase electrical service with a bolted pressure switch and protected by GFCI at the main switchboard. During an inspection, the inspector activated both elevators at the same time (1) 50HP and (1) 40HP and it trips the mainswitch and shuts off the power for the entire building. I believe the GFCI settings are set too sensitive and needs to be adjusted. What is the proper way to correctly set the GFCI settings, so that the in-rush current from the elevators do not trip the mainswitch?
Thanks for your help