I am trying to sort out this GFCI thing. 406.3(D)(3)(b) states that a GFCI can be installed without an equipment ground. Isn't this intented to have the GFCI's placed in bathrooms and kitchens that are two wire? I do not believe that it is to justify installing GFCI's thoughout a house to be able to use equipment that has a ground conductor. Wouldn't that be just as bad as using a 3 to 2 ground plug adapter? I do not believe that allowing that benefits anyone, or am I wrong?
406.3(D)(3) Non–Grounding-Type Receptacles. Where attachment
to an equipment grounding conductor does not exist
in the receptacle enclosure, the installation shall comply
with (D)(3)(a), (D)(3)(b), or (D)(3)(c).
(a) A non–grounding-type receptacle(s) shall be permitted
to be replaced with another non–grounding-type receptacle(
s).
(b) A non–grounding-type receptacle(s) shall be permitted
to be replaced with a ground-fault circuit interruptertype
of receptacle(s). These receptacles shall be marked
“No Equipment Ground.” An equipment grounding conductor
shall not be connected from the ground-fault circuitinterrupter-
type receptacle to any outlet supplied from the
ground-fault circuit-interrupter receptacle.
(c) A non–grounding-type receptacle(s) shall be permitted
to be replaced with a grounding-type receptacle(s)
where supplied through a ground-fault circuit interrupter.
Grounding-type receptacles supplied through the groundfault
circuit interrupter shall be marked “GFCI Protected”
and “No Equipment Ground.” An equipment grounding
conductor shall not be connected between the groundingtype
receptacles.
Sorry cut that off short before I finished. My intent wasn't to just copy code over. I believe the intent is exactly that to allow you to put the three prong receptacles in. Where ever you want. Where is the hazard if GFCI is provided? We can't make people re-wire their entire old house because they want to use three prong appliances. If you have the GFCI it is a LOT safe than the adapter. Let's face it people are GOING to use their stuff. This is the perfect way (requirement) to allow then reasonable easy to make it safe.