A GFCI receptacle will work on a 2 wire circuit (grounded system) without an equipment ground. It senses current imbalances between the hot and neutral, which when present, it will trip. This makes sense to me and there is no less than a thousand articles on this topic. However, my questions is, will a GFCI receptacle work on an ungrounded system?
On a grounded system, to my understanding the leakage would go through the body and into the ground to return to the source, and the resulting imbalance would cause it to trip. Technically there wouldn't be a return path through the ground to the source on an ungrounded system. You would be brought to the same potential, and there wouldn't be shock hazard. Am I right here?
Seems like I answered my question writing this through... To me it seems like GFCIs are useless on ungrounded systems. Actually, can GFCIs even be used on ungrounded systems? There would be no grounded/neutral conductor. Am I going mad?
On a grounded system, to my understanding the leakage would go through the body and into the ground to return to the source, and the resulting imbalance would cause it to trip. Technically there wouldn't be a return path through the ground to the source on an ungrounded system. You would be brought to the same potential, and there wouldn't be shock hazard. Am I right here?
Seems like I answered my question writing this through... To me it seems like GFCIs are useless on ungrounded systems. Actually, can GFCIs even be used on ungrounded systems? There would be no grounded/neutral conductor. Am I going mad?