But this is an interesting bit of electrical theory we've going here.....
It would appear the contention is that gfci's can't work w/o a path for current to travel
So if we've an isolation Xformer (floating in space?) , H&N or H&H going through a toroidal to a load , said load side would need a source to loose current to?
Is that the jist?
~RJ~
Yes, that's why I withdrew my comment. Imagine a current source, panel, GFCI circuit breakers, Romex, etc floating in space. The Romex doesn't have an EGC in it. At the end of the Romex is a receptacle with a toaster plugged in. If we strip the Romex somewhere and grab the hot, nothing happens. We're not touching ground so no flow, except for the capacitance current as we get charged up to the conductors potential, which others have pointed out may or may not be enough to trip the GFCI. Only if I make contact to a ground potential that is connected to the neutral back at the panel will current bypass the normal neutral path and cause an imbalance.
In fact, if I grab the hot and neutral at some location without being grounded, the GFCI won't trip, because now I'm a parallel load to the toaster and the outgoing and return currents are still the same.