Rated/listed enclosure used as a general use locker, cabinet, etc. isn't exactly being used as an electrical enclosure. They better have wiring methods within such enclosure supplying said receptacles that are generally acceptable for indoor locations and not just open conductors emerging from a raceway or cable entering said enclosure.
If they do have just open conductors within the enclosure then it does need to be rated/listed, which includes closing all openings with something that is listed or comparable to the enclosure wall, and need to use proper fittings for entering wiring methods. A sleeve large enough to pass the cord cap through just don't meet such requirements.
If it is not used as an electrical enclosure then it sort of becomes part of the building and not a part of the electrical system. Now you are passing the cord through a floor, wall or other building partition.
Exactly how you wish to observe certain details changes what code section(s) is violated.
Bill did not ask about the sleeve, so I did not get into it.
You are bringing up an issue that the OP was not not asking about.
It may or may not be an issue, but it is distracting from what the OP presented.