Yes it's bad, and the reason I don't trust the test button. There shouldn't be any voltage present on the wipers after the test button is depressed.
JohnJ0906 said:The only test accepted by UL and the GFCI manufacturers is the test button. At least that is my understanding.
If you push the test button, and there is still voltage, the GFCI is bad.
I don't think there is any recognized AFCI "testers"electricmanscott said:That battle actually was over an AFCI breaker but it is the same idea. Test button trips it, end of story.
I bet you thought I was going to mention something about a megger, didn't you?JohnJ0906 said:Howdy, Stranger! :grin:
electricmanscott said:Exactly! And if you are an inspector you should be testing with the button and that's it. I have fought the "Battle of My tester dosen't trip the breaker you have to replace it" and it is very frustrating to say the least.
That battle actually was over an AFCI breaker but it is the same idea. Test button trips it, end of story.
Because there is no other way to make a plug in GFCI tester work. I has to create leakage to ground to test the device and the only way to do that is to use the grounding socket on the receptacle. If there is no EGC, the tester cannot work."Why do these testers look for ground when a GFCI was intended to work/trip to a fault on a two-wire circuit?
don_resqcapt19 said:Because there is no other way to make a plug in GFCI tester work. I has to create leakage to ground to test the device and the only way to do that is to use the grounding socket on the receptacle. If there is no EGC, the tester cannot work.
Don
JohnJ0906 said:If the tester faults from hot to neutral, then you have a short circuit, not a ground fault - the GFCI isn't looking for that. So it has to do a hot to ground. If there is no EGC, then obviously, there won't be a ground fault. Where is this ground path coming from - it's only a hand-held tester.
On a no EGC circuit (2 - wire), use an extention cord from an outlet with an EGC, and use a wiggy tester from the outlet you are testing (hot) to the extention cord (EGC). Now you have a ground path, and the GFCI will trip.
76nemo said:What do you mean? A GFCI is, or at least thought it was, designed to look for an imbalance on the grounded leg. Are you saying I am wrong?
76nemo said:Let me make this simplier, is anyone saying a GFCI will not truly respond to an imbalance to the neutral/grounded?
Yes I am...it is designed to look for a difference in the amount of current flowing on the ungrounded and grounded conductors of the circuit.What do you mean? A GFCI is, or at least thought it was, designed to look for an imbalance on the grounded leg. Are you saying I am wrong?
76nemo said:What do you mean? A GFCI is, or at least thought it was, designed to look for an imbalance on the grounded leg. Are you saying I am wrong?
They could make them out of metal, and require the operator to be bare-footed.JohnJ0906 said:Without an EGC, how can the plug-in tester create an imbalance?
JohnJ0906 said:A GFCI is looking for an imbalance between the ungrounded and grounded conductors. It does not require an EGC to do this The built-in test button does not require an EGC to properly test the GFCI. Plug-in testers do require the EGC to test the GFCI. Without an EGC, how can the plug-in tester create an imbalance?
76nemo said:Beee-eye-N-Gee-Ohh, spells bingo. Why not have the ability to test two-wire?