stickboy1375 said:You are so OVER THINKING this...
Overthinking is how I differ from the rest. I try to analyze theory much more than some others to trigger my remainders:wink:
stickboy1375 said:You are so OVER THINKING this...
How does the average home owner who's "supposed" to test them monthly know that it's still hot even though it snapped??JohnJ0906 said:If you push the test button, and there is still voltage, the GFCI is bad.
They can't design a GFCI tester to work like a GFCI test button????stickboy1375 said:Your correct in your thinking, the problem is how would a two wire tester create that imbalance without the ground? Answer that question and you have your answer.
wptski said:They can't design a GFCI tester to work like a GFCI test button????
JohnJ0906 said:Where is the ground path that the tester will utilize? The test button shorts (with a resistance) from load hot to line neutral. This bypasses the measuring electronics, and creates an imbalance on the load side - current goes out on the load hot, but doesn't return on the load neutral - imbalance. The plug-in tester can't do this.
As I posted before, use an extention cord plugged into a receptacle that has an EGC, and use a wiggy, if you can't trust the GFCI.
Right, it's through a person most normally. That would be one silly tester, wouldn't it?76nemo said:So in a ground fault, where does the fault scurry to in two-wire? It's not through the ungrounded?
Where does a diagram show that there is any circuit bypassed by the test button? Unless the diagrams posted in other threads lately are too basic.JohnJ0906 said:Where is the ground path that the tester will utilize? The test button shorts (with a resistance) from load hot to line neutral. This bypasses the measuring electronics, and creates an imbalance on the load side - current goes out on the load hot, but doesn't return on the load neutral - imbalance. The plug-in tester can't do this.
As I posted before, use an extention cord plugged into a receptacle that has an EGC, and use a wiggy, if you can't trust the GFCI.
wptski said:Where does a diagram show that there is any circuit bypassed by the test button? Unless the diagrams posted in other threads lately are too basic.
Thanks for the slide show! Interesting graph also which I've seen before about trip time of "typical" GFCIs. Not all are within typical values shown.480sparky said:Try clicking here.
My thanks as well, 480. Pages 38 and 41 raise a question in my mind, however. On page 38, they state that using a GFCI tester on a 2 wire circuit can be dangerous, without saying how or why. Then on page 41, the question "What if there is not equipment ground....? Such as in a 210-7(d)(3) application?" appears but is never answered. Any idea why the use of a tester would be "dangerous? (I've seen inspectors use 'em on more jobs than I can count). Also, any thoughts on the Art. 210 reference?480sparky said:Try clicking here.
lbwireman said:My thanks as well, 480. Pages 38 and 41 raise a question in my mind, however. On page 38, they state that using a GFCI tester on a 2 wire circuit can be dangerous, without saying how or why. Then on page 41, the question "What if there is not equipment ground....? Such as in a 210-7(d)(3) application?" appears but is never answered. Any idea why the use of a tester would be "dangerous? (I've seen inspectors use 'em on more jobs than I can count). Also, any thoughts on the Art. 210 reference?![]()
Sorry 480, I should have been clearer in my post. My intention was to thank you for the link to the NEMA slideshow, not hold you accountable for its' content. Beyond that I had hoped that you or some of the other folks on the forum might have some thoughts as to why it might be "dangerous" to use a tester on a "2-wire circuit" (presumably using a 2 prong/3 prong adapter), as well as any thoughts on the Article citation. Most of our work is service, upgrade and retrofit in an area where the majority of the occupancies are more than 50 years old, so I encounter and have a particularly keen interest in grounding and bonding issues. One of our most common "bread and butter" jobs is device replacement under '05 Art. 406.3(D)(3)(b)&(c) which used to be 210.7(D)(3), so I was interested to know if anyone had any ideas as to why the question might have been put in the NEMA document (and then left unanswered). No offense was intended.:smile:480sparky said:Since I didn't write it, I can't answer for them. But a plug-in GFCI tester will not work on an ungrounded receptacle.
don_resqcapt19 said:The safety problem with using a GFCI tester on a circuit that does not include an EGC is the fact that the tester will put 120 volts via a resistor onto the EGC. If the device being tested is a 3 wire receptacle and there is a load that has a 3 wire cord plugged into the other half of the receptacle when you use the tester the case of the item that is plugged in will be energized at 120 volts.