Not likely. There is also coupling to the earth.Will the 10-2 keep it from tripping? ( not code compliant move gfci i know that )
The AC current through a capacitor is proportional to the AC voltage across it. And so even if the hot and neutral conductors have the same capacitance to ground, there will be significantly higher current through the L-G capacitance than the N-G capacitance on a relative basis. Very little current will flow through the N-G capacitance because the N-G voltage should be quite small. This will cause the current through the line conductor on the GFCI output to be higher than that in the neutral conductor, and it will cause the GFCI to trip if the current through the L-G capacitance it sufficiently large.200' A GFCI works on the inbalance of current on the hot to grounded conductor . on a two wire uf cabel what conductor is higher current ?????? ( capacitive coupling )
NO neutral in this circuit !The AC current through a capacitor is proportional to the AC voltage across it. And so even if the hot and neutral conductors have the same capacitance to ground, there will be significantly higher current through the L-G capacitance than the N-G capacitance on a relative basis. Very little current will flow through the N-G capacitance because the N-G voltage should be quite small. This will cause the current through the line conductor on the GFCI output to be higher than that in the neutral conductor, and it will cause the GFCI to trip if the current through the L-G capacitance it sufficiently large.
Why do you think not code compliant?Will the 10-2 keep it from tripping? ( not code compliant move gfci i know that )
So you have a 2 pole (240V??) circuit fed by a GFCI. However you don't need the neutral. You used a 10-3 UF conductors, so the _cable_ has hot-hot-neutral-EGC?
I'd suggest cheating a bit and running the two hots on the conductors symmetric to the EGC. This probably means 1 hot on the black wire, 1 hot on the white wire, the EGC sitting between them, and the red wire sitting unused off to one side.
This would make the system balanced around the EGC, making the capacitive coupling invisible to the GFCI (because you will see the same current from the black hot to EGC and the 'white' hot to EGC.
Just went to look at a piece 3 wire with ground UF cable because I didn't thin your picture looked like what I am used to seeing.Thinking along the same lines, when using the black and red wires for hots it might be helpful to connect the white wire to the ECG. I think that should provide more symmetrical capacitances than just leaving the white wire floating.
What is it supplying?
if i use # 10-2 uf with no egc will it work
I thought he was saying placing the GFCI at the load end of the run was what wasn't compliant and that is what I was asking about. Very few cases would it have to be at the supply end of a circuit outside of maybe some art 680 or 682 applications.OP asked:
10-2 without an EGC is not compliant.
On the other hand 10-2 with EGC but without a neutral is perfectly fine for a straight 240V load.
Jon
Piece I looked at had black and white as the two outer conductors, the red was next to the black and of course the bare between red and white.
I think they all are typically that way.
no stranded conductors (that would be nice sometimes) but yes colors arranged in that order.