ELA said:
So in the case where the breaker trips due to noise it is not considered defective but instead not immune enough for the level of noise it is exposed to.
As one example I had a 3 phase GFI tripping intermittently. It was replaced twice with the same manufacturers brand and continued to trip. We then replaced it with a different model that had specifically been tested for noise immunity and it held fine.
QUOTE]
You have just disputed your own contention that nuisance tripping is "for real"
The breaker was not "suitable" for the application to which it was applied, therefore it tripped. Re-read your post and you may understand the fallacy of your statement.
Sorry but your logic escapes me. And your tone .....
Any given part may perform just fine in a design in 98% of the applications where installed. Then in 2% it may fail due to the presence of a larger than normally encountered electrical interference level.
The usual solution would be to filter or eliminate the source of the noise.
In the example I cited the customer was not willing to find the source and filter it so we had to do extensive research to locate a more robust breaker.
Unless equipment is required to undergo extensive EMC testing (like it is when required to be CE marked) then you may never know there is an issue until it is installed in an electrically noisy environment.
Manufacturers may not always know in advance what the noise levels at an installation site may be.
Take another example:
RF from hand held radios are notorious for inducing currents into electrical equipment and causing upsets. And yes they can cause a GFCI to trip.
So a given piece of equipment uses a GFCI that performs just fine up until when a service person keys up a radio in the vacinity of the breaker and it trips. This is a nuisance trip.
The breaker is reset and never fails again during its lifetime (provided not exposed to a high level of noise).
Nuisance tripping is very real and you would know that if you understood EM compliance.