LarryFine
- Henrico County, VA
- Electrical Contractor
I disagree with that statement.The ground fault looks for the exact same current to "comeback" as has left, therefor IMO a fault could occur in either wire to ground and trip the gfi.
The grounded conductor has much lower impedance (theoretically - let's ignore conductor voltage drop) than your body plus the grounded surface it's in contact with during the shock.
Contact (accidental, let's say) with the load-side grounded conductor of a GFCI won't produce enough current to trip it. It must be an energized wire you contact to get zapped.
If a wire makes accidental contact with the drill case, the resultant voltage to earth depends on where it is in the drill's circuit: if it's the hot wire, it's 120v; if it's the grounded wire, it's 0v.
Presuming linear impedance throughout the motor, it will act as a linear voltage divider, and the shock current will depend on the relative voltage to the grounded surface being contacted, because of where the contact is.
If the grounded conductor happens to be the one contacting the drill case, there will be no shock, just like touching your meter base or the panel neutral bus (and remember, we're talking theoretically - no neutral-EGC sensor.)
Now, if we have such an undiscovered contact in the drill, and you reverse the polarity anywhere in the circuit (i.e., either line or load side of the GFCI), the ungrounded conductor is suddenly the one making contact.
Now there's a potential between the drill case and earth, building, etc.; what happens next depends. With an intact EGC, the circuit will trip the moment it's plugged in (if ahead of the switch), or when the trigger is pulled.
Without an intact EGC, the GFCI will trip either when the drill is picked up and ground contact is made, or after pulling the trigger and ground contact is made. Of course, the current depends on potential and impedance.
Again, there's no potential to drive a current through the body, so there's no divergence of current for the GFCI's CT to detect. In other words (and my apologies to my grammar teachers), there's no current to not return.The GFI should see neutral current "NOT RETURNING" if the neutral is grounded downstream. A fault in either wire will trip the GFI, or at least in theory.
Added: And, as I often say, GFCI's don't work on non-grounded supplies, nor are they needed, since there's no pathway to allow a current, and no voltage to drive it (capacitive or inductive coupling aside.)