2 pole 50A 30ma GFCI. Will the test button work if the white wire on the Breaker is not connected?
the internal run from 120vac, but with a 2 pole ocpd you technically do not need the CT to power the internal electronics (from a ckt design perspective). i am kinda baffled as to why they have a N tail on a 2 pole gfi ocpd.
You most definitely need the neutral for the GFCI to function.
See this thread:
http://forums.mikeholt.com/showthread.php?t=186853
the internal run from 120vac, but with a 2 pole ocpd you technically do not need the CT to power the internal electronics (from a ckt design perspective). i am kinda baffled as to why they have a N tail on a 2 pole gfi ocpd.
Use of same internals as what single pole units use is less parts to need in inventory?agree, with existing ocpd's. thats not what i meant. with a 2 pole you can make the internals run just fine w/o connecting back to the CT (N).
you think the 1pole internals is the same as 2pole internals?Use of same internals as what single pole units use is less parts to need in inventory?
I wasn't saying the entire thing is the same, was suggesting that using same components within both whenever possible seems like it would be economically feasible.you think the 1pole internals is the same as 2pole internals?
you think the 1pole internals is the same as 2pole internals?