Boy I sure would like to know what that means and how a cheaper GFCI has more problems with it.
I see large pipe threaders and large chop saws on GFCIs all the time without any issues.
Bob this problem is not new, it's been around for as long as GFCI's have been required, it has only be recently (in the last 10 years) that UL has been trying to address the issue in requiring GFCI's to have a design to lower the neusent tripping that this problem was causing, mostly because of the manufactures and code making panel wanting to expand the use of GFCI's into areas that was exempt for the requirement.
I identified this problem over 15 years ago for my own knowledge, using a capture scope with recording and a simple plug in motor to show how the high frequency pulse on a circuit can look like an imbalance to the GFCI circuit by not being in phase with the 60 Hz, the problem with this was easy to solve since this event was a one time shot if no residual resonance were to occur, but that is not always the case, other factors such as reactant and other things can cause harmonics to keep the spike going for a few cycles after the initial event, some will call this a ringing transient, this provided another problem to solve, well it was discovered by doing a gated time delay to delay the trip after a set time that would allow all oscillation to cease before allowing the electronics to view (monitor) the circuit after an event was the best answer to resolving the problem, so they redesign the National GFCI IC chip (LM1851) with this gated feature (some just call it a time delay) and most GFCI manufactures jumped on board to use this as well as other filters and TVSS devices to limit the nuisance tripping to come in to compliance with UL specifications for the newer GFCI's some of the other change in requirement was the neutral grounding issue and the detection of miss wiring which was also just lately incorporated in to them.
Much of this was posted in here a while back not sure if it was before the forum change of 2003 or not, but over the years I have posted about this problem allot.
Now that brings us to these what I call cheap Menard's GFCIs, well in the past couple years I have been finding them, and it not just from Menard's, CES has a version of them too, that have been quite a problem with inductive loads, not too long ago I posted a problem I encountered in an apartment building where the maintenance workers were using these to bring the apartments up to code to meet their HUD requirements, this was my first most profound experience with them, and I sent a few samples of them as well as some I went and purchased from Menard's, to UL for further analyzing, well the only thing I ever heard from UL on this was they were still trying to track down where in China they were being made, because these units were not using the UL listed National chip LM 1851 and didn't seem to have the delay that helped in stopping this problem, I have not made any more inquiry's to UL about the problem, but maybe I will after I get through this VFD install I'm working on.
Here is little of what Samuel M. Goldwasser had put in his book "Notes on the Troubleshooting and Repair of Small Household Appliances and Power Tools" back in 1996:
Why a GFCI should not be used with major appliances
A Ground Fault Circuit Interrupter is supposed to be a valuable safety device. Why not use them everywhere, even on large appliances with 3 wire plugs?
A properly grounded 3 prong outlet provides protection for both people and the appliance should a short circuit develop between a live wire and the cabinet.
Highly inductive loads like large motors or even fluorescent lamps or fixtures on the same circuit can cause nuisance tripping of GFCIs which needless to say is not desirable for something like a refrigerator.
Nuisance tripping of GFCIs
When used with highly inductive loads like motors or even fluorescent lamps, GFCIs may occasionally (or more frequently) trip due to the voltage/current spikes at power on/off. While the NEC/UL specifications apparently allow for some time delay in their response to combat this problem, it is not known if all manufacturers of GFCIs incorporate this into their product. However, the very common Leviton GFCI outlet probably does use the National chip (LM1851 Ground Fault Interrupter) referred to below. Also see the section: How does a GFCI work?.
(From: James Phillips (jamarno@juno.com).)
I quit having GFCI trouble after I fixed all the bad wiring connections, and I haven't had trouble at all with GFCIs and my workshop, which I wired myself. GFCI controller chips include a time delay to reduce false tripping. I used to think GFCIs always tripped at 5 to 6 mA, but the UL allows up to a whopping 200 mA if the GFCI stops the current within 30 ms, and 6 mA leakage is allowed to last 6 seconds.
According to National Semiconductor, their GFCI chips will stop a 200 mA fault in 20 ms, a 6mA fault in .5 sec.
And can be read in full
HERE
Remember much of this book was written back before many of the newer requirements so his suggestions are not up to date to the newer requirements.
I do want to state that the other problems that you and other have mention are as real as this also, and have to be dealt with as needed just as finding any solution to a problem.
One of the most common symptoms of an inductive kick back is the very noticeable (if you look for it) tripping when power is removed from an inductive load, generally it does not occur when power is applied, this is a good telltale sign to the problem.
I know this was alittle long winded, but I hope I could share this info with the forum to help others in the understanding of this problem, and short cut some of their trouble shooting time.