My point is that it is not required to trip in a 1/2 cycle...the permitted trip time at 5mA is 7.2 seconds.1/ 2 cycle is much faster in NY hardly enough time to feel the shock.
It is not needed to make the GFCI work, but it is required by the code for some equipment. See 250.114.The manufacturers instructions say to hook up the ground if it is there. Why bother if it is not needed??
As far as what happened to you, we have no idea of the exact conditions, but a working GFCI will trip when the currents are not matched between the hot and the neutral, with or without an EGC. If the source of the shocking current was the hot that was supplied through the GFCI, then the device will trip.I certainly do not need to try it again.
If this is a double-insulated tool, there is no EGC in the power cord, so that would have made no difference. You got a shock because of the water providing a pathway from the tool's internal energized parts, most likely the switch. (I know you know this already)quogueelectric said:Hilti gun you know red PLASTIC in the pouring rain
That your link to the gfi explanation before was probably the best single laid out presentation of how a gfi works. However it still does not explain the shock. You have heard of a New York minute? It is such a simple thing to connect a ground to a GFCI at the panel I would rather have a nuisance trip Than a nuisance electrocutionroger said:So you are saying EGC would effectively bond this plastic tool. The GFCI may not be the only thing that you did not understand in your test. :grin:
Roger
quogueelectric said:However it still does not explain the shock.
quogueelectric said:It is such a simple thing to connect a ground to a GFCI at the panel I would rather have a nuisance trip Than a nuisance electrocution
my real life experience is why did the rules change when I hooked up the ground. I have been very precise in explaining the surrounding circumstances. Are you an amprobe? Because I would like to know how you know how much current was flowing through you. Maybe you went to neutral and the gfci saw you as a toaster oven.mayjong said:wow! just realized how far this thread had gone..
the description of the fork and knife tester was a joke, BTW.(duh)
sorry quogueelectric, if you got shocked but i'm pretty sure most of the folks on this board have, too.
my experience with a gfi was much the same as yours, yet the one i got hit by HAD a ground wire. by your logic, that should never have happened! the shock i recieved was much longer than 1/2 cycle... the test button and my tester both tripped the gfi (after the lovely hit) and this wasn't years ago, it was just a couple weeks ago.
5-7 mA , in case you don't know, is "very uncomfortable" and it would take almost 10 seconds to trip a gfi -by then, i would hope, you(or I) would let go!
and, without a ground wire, they will trip... think about it- if you are getting shocked, there is a ground, yes?
it's you....
quogueelectric said:There must be a thousand posters on this site who are capable of duplicating this circumstance and noone probably will ...........
I have no doubt that you recieved a shock, but that does not mean the GFCI was not doing its job. For the most part all a GFCI does is limit the duration of the shock. My guess is that because of the better path via the equipment grounding conductor the GFCI tripped much faster than it did when the EGC was removed. Remember that the GFCI is permitted to take up to 7.2 seconds to open the circuit at 5mA. You would drop the tool in a fraction of that time. With the EGC in place it may have tripped fast enough that you did not even feel the shock, but with a limited ground fault current path the time to trip goes up.As far as being repeatable or testable There must be a thousand posters on this site who are capable of duplicating this circumstance and noone probably will because they dont believe the outcome so it goes by the wayside oh well we are all to busy.
While it may trip that fast it is permitted to take up to 7.2 seconds to trip at that current level.It is able to sense a mismatch as small as 4 or 5 milliamps, and it can react as quickly as one-thirtieth of a second.
quogueelectric said:They told Columbus the world was flat didnt they and all the sheep believed in that.