Are GFIC mandatory for every receptacle in a commercial kitchen? Some keep tripping for the refrigerators, Warners, etc., and I would like to go with standards ones for some of the appliances. First time doing commercial and I am curious
...
audible alarm gfci receptacle
http://www.legrand.us/passandseymour/gfcis-outlets/audible-alarm/1595traw.aspx
If the GFCI is tripping for the equipment, look for the reason. The GFCI is doing its job.
I have started to use those for receptacles intended to supply refrigerators and freezers where GFCI is necessary, not really that much more then the cost of a regular GFCI receptacle and costs nothing extra to install.For the refrigerator, offer to install monitoring equipment. There are some devices that are cheap in price (basic in notification), and expensive (extensive in notification).
If the GFCI is tripping for the equipment, look for the reason. The GFCI is doing its job.
For the refrigerator, offer to install monitoring equipment. There are some devices that are cheap in price (basic in notification), and expensive (extensive in notification).
Make sure to have him sign a piece of paper that says he is at least as liable for any injury or death that could occur as you are for doing this, in hope he will get the message. If he would happen to agree, I still wouldn't be very willing to remove the GFCI's, really cheap ones may be questionable, but all the well known brands generally do what they are supposed to do with little false tripping.Thanks. The chief engineer asked me to remove GFICs in this kitchen and install the standard ones. I just starting working here after coming from retirement in residential and I am really uncomfortable in doing so, but the audible ones are a marvelous idea and I will try to sell those to him. THANKS a lot.
"For the refrigerator, offer to install monitoring equipment. There are some devices that are cheap in price (basic in notification), and expensive (extensive in notification)"
Would you guide me in this type of monitoring equipment? Photo? Web site?
Thanks,
Quick search I came up with this for something pretty inexpensive, or you could probably go with something more sophisticated and more expensive and even capable of calling you when it goes into alarm.
...
As far as removing the GFCI, there is not a chance I would do that. If the chief engineer wants to remove it they will have to do it themselves. Regardless of any paper work I am legally and morally responsible for the work I do. Sorry if that sounds over the top but do not remove GFCI protection.
I wouldn't remove the GFCI either, was mentioning the paper as more of a threat to hopefully wake up the engineer that suggested removing it.I agree, you can get anything from a basic battery powered magnetic alarm to very sophisticated systems.
They can dial out or email out or blue tooth connect, wifi connect etc.
I suggest Goggling 'freezer alarm system' or 'refrigerator alarm system'. There are many available as many restaurants and medical facilities use them.
As far as removing the GFCI, there is not a chance I would do that. If the chief engineer wants to remove it they will have to do it themselves. Regardless of any paper work I am legally and morally responsible for the work I do. Sorry if that sounds over the top but do not remove GFCI protection.
Sorry to continue in this matter, but he mentioned that the reason the GFIC are tripping is because those appliances pull to much current (?), maybe I am wrong but is there is too much current the breaker will trip and the over current has nothing to do with the GFIC ... Does it? He has been as a CE for many years, I respect his opinion but .....
GFCI is not an overcurrent device, and should carry overload conditions indefinitely - or at least until the overload condition causes other problems that turn into ground faults.Sorry to continue in this matter, but he mentioned that the reason the GFIC are tripping is because those appliances pull to much current (?), maybe I am wrong but is there is too much current the breaker will trip and the over current has nothing to do with the GFIC ... Does it? He has been as a CE for many years, I respect his opinion but .....
Sorry to continue in this matter, .
I wouldn't remove the GFCI either, was mentioning the paper as more of a threat to hopefully wake up the engineer that suggested removing it.
When I showed him the subpanels where those circuits for the GFICs where (after many years he didn?t know) he went berserk because many of the breakers are 15 Amps and told me to replace those for 20 Amps breakers because in commercial facilities shouldn?t NEVER-EVER have 15 Amps breakers!